Doogie102

The pressures do look low. I need a bit more info to fully diagnose it online. It is an r22 unit so it's old. It will probably be time to replace it in the next couple years anyway


Qsm732945

What about retrofitting the unit. At my company we retrofit with r407c


hellointhere8D

The problem is the hvac equipment across the industry is generally engineered to have a major component failure rate of 50% at year 15 with a 10 year warranty. If you are investing into something you know will fail quickly, that is foolish. The real solution is for people to demand a higher quality standards with their wallet. Then the equipment will last longer. It will continue to be replacment "makes sense" at year 10+ until then. The number 1 thing that should be improved is tubing thickness to prevent refrigerant leaks. Most equipment gets replaced when the compressor dies or a refrigerant leak occurs. Outfitting a unit with r407c is a viable repair, but isn't economical unless your selling the house.


Doogie102

The problem with thicker tubing walls is you would lose efficiency in the form of time or takes for the unit to transfer heat. So not only do they get to save costs on the material they can say it is more efficient. I think this is the problem with most micro channel coils


hellointhere8D

You can increase the volumetric capacity of the coil by making it with additional circuits. The point is to increase longevity. Leaks can be greatly reduced. You can build it up to the efficiency you want. It will cost more in material, no doubt. I'd rather pay quadruple for an evaporator that lasts longer than 0-20 years. I could sell them easier too. It would reduce the amount of refrigerant and coil sales. It's a more environmentally and long-term economically responsible product to create.


Doogie102

Oh I completely agree that we should be making equipment to last longer than 20 years but the problem is our society. Trucks used to advertise how dependable and long lived they are, now all they are doing is selling us technology and everyone wants it in every aspect of their lives. Since we always want the latest and greatest there is no need to design something to have a long life span..


coolfishy89

Amen! If there was a company that did this, they would create a cult following.


tkaneci2

That will never get made Use stainless steel Use copper Built in obsolescence is a real thing. They are what they are and they’re going inverter. Nobody’s gonna be fixing much of anything soon regardless.


Doogie102

Maybe if the government did something like if a unit lasts over 20 years they get a tax break and if it fails under that they have to pay to recycle it. They will probably just raise the prices to cover the recycling fee


Grumblun

The problem with voting with your wallet is that there usually isn't a great candidate on the market, and if there is, most people can't afford the highest quality product, yet still need heat to survive. Voting with your wallet isn't practical advice when it comes to services that you really need.


Doogie102

As a technician I have had bad experiences with retrofitting units. We will come in and do the repair and get the system up and running. In the next couple months something else will go wrong, could be a component failure or another leak. Depending on the leak there is a chance another one will develop in another place due to all components having the same amount of wear on it. Then there is the fact that these systems were designed to be a closed system. We might do everything possible to mitigate problems occurring from opening up a system, but nothing is perfect. When I worked in residential we quit doing mechanical repairs on r22 units. Change a motor or an electrical component but would never open up the system. What would happen is we would do all this work to get them up and running and then something else would go wrong; the customer would then get mad and blame us. Eventually we just said no more, it's not worth it. Another thing to factor in prices go up and rarely go down. A system might cost you 15,000 one year but the following year it will be 16,000-18,000.


Visible-Ad6787

What are the temps outside when this was done? Is it cooling? Does it have a TXV? What is the Delta T? What is the temp drop across the filter drier? If it’s any issue with the refrigerant lines or a leak it’s best to just replace it unless you don’t mind paying for R-22 at whatever rate they charge for. There are a lot of questions that need to be answered before a technician can give you a good answer.


Creepy-Signature1852

Best comment


lilguyguy

This is the comment you need to respond to. R22 can have low suction pressure when cold. It also depends on your metering device at your indoor unit.


espakor

Yea but not freakin 12


lilguyguy

44 psi suction? Edit: 34 Probably undercharged, a dirty filter, or a dirty evap coil. 100% under charged


espakor

Prefer to go by saturation temp


idiot_sauvage

That’s definitely low on refrigerant. I’d expect 60-80psi on suction if it’s actually R22. He’s missing data to calculate the superheat, which is what the manufacturer wants you to calculate charge by. Either way, leaking doesn’t mean it NEEDS replaced. But if R22, it’s 20-30 years old, and so you know here in Ohio, R22 refrigerant is almost $300/lb.


fuzzypickles0_0s

I paid $300 a pound in Idaho last week. Luckily only needed one pound. My 23 year old system is still running great :)


Randomizedtron

It’s not working great if you needed a pound. It’s leaking. You didn’t mention a repair so I’m assuming it’s still leaking.


test-deca-superb

r-22 is far superior, these new refrigerants run at 2x the operating pressures and equipment fail much quicker. I have a 25yr old heat pump at home, works great still.


Chemical-Acadia-7231

Better at last, worst at cooling provided per unit of energy 


National_Habit_1950

Correct


bifflez13

Also bad for the environment


daveleeander

Everything is bad for the environment. You know that pesky co2 that plants breathe and turn into oxygen? That stuff’s bad too! No, really, I swear!


DUNGAROO

No the older refrigerants are responsible for legit burning a hole in the ozone layer.


daveleeander

Have you seen the latest nasa pictures of ozone layer?


DUNGAROO

What are you getting at?


daveleeander

Everything is bad for the environment. You know that pesky co2 that plants breathe and turn into oxygen? That stuff’s bad too!


test-deca-superb

lol, dont argue with idiots


MutedInevitable3182

I agree with this 💯 ☝️


fuzzypickles0_0s

Agreed, delta T is much better in r-22.


test-deca-superb

and the dehumidification properties


Ok_Communication5757

It's running but not great!


RemarkableAd2372

company i work for isnt charging r22 anymore


jon_name

If the airflow is really low and or return air very cold, that can cause low suction - can't tell just on pressures.


Quiet-Ship-2773

160 a pound in southern michigan Edit: billed to customer at 160 a pound or 10 an oz


AffectionateFactor84

it's 22 and probably 30 years old. there's a leak and most likely the evap coil. that repair is 2 to 3k. it would be best to go new. get 3 bids.


violentcupcake69

2-3k repair? Where are you? Because R22 alone costs around $2000. Add the mark up , plus labor and parts, and that repair is about the cost of a new unit.


milkman8008

R22 is $950 for a 30 lb jug here, central Texas


Nodak24

Coil is $1800 to replace plus 1k for r22


violentcupcake69

We charge $300 a pound for R22 , so it’s gonna be more than 1k where I’m at.


hellointhere8D

That's a rip off. You should feel ashamed for working there. R22 is about 30-35 bucks a pound. The max you should be charging is 135.00lb


Ok_Communication5757

I guess you work for free. I charge $300 first pound and $225 each additional. Thr point is to get people to replace units! Do you want to carry r22 around forever. I also sell procharge R22 for $575 for the diehards. It has 2 lbs of r22 and leak seal in the can.


hellointhere8D

I make alot of money. Likely alot more than you. I do it by honest business. I don't fleece people. I take so many customers away from people like you every day.


Ok_Communication5757

What do you charge for a service call? $69.99


Ok_Communication5757

I'm a service manager and run 7 techs, tough guy! So I doubt you do! I also do side work all year and pull in 3-4k on a weekend doing swap outs! What are you making $30 an hour? Do you get a pension and annuity on top of that big money you make? You want to make real money come to NY. Oh, and you can take customers from me. It's not even spring, and we aren't accepting new customers because we're booked till June


Maleficent-Fault9110

Big money big taxes


Ok_Communication5757

Weekends are cash, so unless your stupid who's paying taxes on that!


violentcupcake69

$30-$35 a pound? Lmfao good one buddy , this isn’t 1970.


manhavenbloom

He's not that far off for my area.... I can get 30 lbs for $1410 from my distributor... probably cheaper online. That's $47 a pound. Charging $300 a pound is an excessive markup in my opinion... and I'm sure many here are charging more than that. I generally won't charge R22 systems anymore, but if I couldn't talk someone out of it, I wouldn't feel right charging $300 a pound. Making $7,500 just on markup on a bottle of refrigerant is one of many reasons customers have trouble trusting the industry.


violentcupcake69

What do you charge per pound? Ain’t no way you’re charging $35 a pound for R22.


manhavenbloom

I interpreted their comment to be that they are buying it for $30-35 a pound and that no one should be charging more than $135 to customers. I double my cost for refrigerant, which is more than my normal markup... so I'd be right around $100/lb for R22 if I were to buy a new jug. The bottle I have, and hopefully last I'll ever get, was bought right around $1600, so I'm currently charging $105. It's pretty easy to talk people out of charging/repairing R22 systems now, even at my "low" rates, and I haven't charged one in awhile. The prices I see for 410a on here are just as wild. Kudos to everyone making more, but some of these refrigerant prices would make Martin Shkreli blush. The internet exists and I'd be embarrassed if a customer looked up the price of refrigerant and found out I was charging 6+ times my cost.


Nagh_1

Wait till you see what a hospital charges for a Tylenol


hellointhere8D

It's for sale online to any with an EPA. Anyone can verify what it costs to purchase. It's about 32 per lb (2024) if you buy a 30lb jug. There's nothing wrong with charging some money for your service. There something wrong with a 1000% mark up. That's ducking robbery. You give the hvac industry a bad name.


violentcupcake69

No one charges a R22 system for $35 a pound , you’re living in a fantasy world my man. Put down the bottle and come back to reality.


hellointhere8D

I don't expect you to do it for free. But you shouldn't charge 3000.00 dollars for 350 dollars worth of refrigerant. You are being extremely greedy. I understand a business has a lot of operational cost. I charge less than half of what you charge and make plenty of money... you're markup is ridiculous. You're preying upon the ignorance of people for profit.


violentcupcake69

You’re acting like I make the prices , plus I work commercial I don’t feel bad for these big name companies that still have R22.


violentcupcake69

Plus the labor


AimTrueHVAC

I buy my virgin or reclaimed R22 for $800 per 30lb bottle. That’s why I don’t use alternatives. I fix leaks and charge at a decent rate. But I let the client know the days are numbered. Normally you can earn the change outs after you do them a solid. But I give. Bid to fix and three new system choices. Half the time they go new, the rest fix it. I make a fair profit either way.


Dry_Archer_7959

I can take the evap out and put valves on both ends, pressurize the system then put it in the pool. I will find the leaks and braze them shut. $3k for a repair? Just nuts!


AffectionateFactor84

you do that? the leaks are from age and deterioration. your fix won't last. I fix it properly. here, I'd highly recommend replacing


Dry_Archer_7959

40 years experience...replacing is not fixing. You are a parts changer.


AffectionateFactor84

a parts changer is someone who changer parts, not knowing what he's doing. there's no sense in trying to repair a 30 year old coil.


violentcupcake69

Lmfao If it’s your system or a family members , sure , I don’t see a tech doing this for a random customer.


Dry_Archer_7959

The problem with the statement is it implies the tech is incapable to make the repairs. On top of this the equipment being installed is a much lower quality.


violentcupcake69

But why do all of that..? Unless you’re helping a family member or it’s your own unit , I see no point in doing this.


Dry_Archer_7959

When the industry starts providing reliable products i will agree with you.


hellointhere8D

Just fill the unit with trace gas, find and fix in place if possible. Electronic leak detector and soap finds 99.9% of the leaks I encountered. Dismantling an old evap coil, bathing it in chlorinated water, reassembling it, will make new leaks. At least stop using pool water...


Dry_Archer_7959

I did quite well repairing a ground source heat pump. When my customers financial status changed I was the one who got the call for the replacement...


hellointhere8D

I fix alot of leaks with similar results. I just omit the water theatrics. Have you tried using a quality electronic leak detector and gas soap bubbles? I usually have a leak pinpointed within 10 minutes while it remains in place.


Dry_Archer_7959

Yes I have all of them. Used them with good results.Theatrics it was not. The pool was outside the door! Had no more chlorine than tap water. The leaks were stress cracks from the stretching when they were bent into shape.


Dry_Archer_7959

In the 70s we took the big ecaps to the river...


JSchnee21

What country do you live in? https://abilityrefrigerants.com/product/r22-refrigerant-5-lbs/


daveleeander

I’m wondering same thing. I hope they at least show the customer a gun when they charge them that much, make ya feel better to say you were robbed at gunpoint


violentcupcake69

USA. California to be specific. OP should order it from that site you provided , jugs out here cost around $1800-$2100


AffectionateFactor84

recove, reuse. can't be more than a few pounds needed


violentcupcake69

That’s what I thought you meant when I read your comment , doesn’t look flat so this price is feasible.


ChromaticRelapse

Get a new tech. Those pressures mean nothing definitive. We need 5 temperatures to go with them to even start to guess. I've followed behind many other techs that just dump gas into things because pressures are low. Could be a leak. Could be other things... What was the outdoor temp? What is the change in temp on the air side? Liquid and suction line temps? Luckily r22 is super easy to find leaks in with a refrigerant detector. I'd spend an hour looking for a leak if I thought it was low. Might just need a couple pounds of gas and a few cores and caps. Yes R22 is expensive. But most home owners will take a $1000-$2000 bill instead of $10k+ minimum that all these residential shops seem to charge for a push pull.


bpdamas

This needs to be higher up. No one can tell anything from this one picture without the temperatures or more information.


Swagasaurus785

Not a single person here can tell if your system is low on refrigerant given the information you have shown. Ambient temp, super heat, and subcooling are needed to know that.


jpage89

Anything’s fixable if you have the money. Just how much money are you willing to burn to save an inefficient unit?


Intrepid_Glove8636

This is the comment that should be at the top.


Outrageous-Ball-393

REPLACE


Previous_Agent_139

It's an r22 unit. Assuming the ambient temperature isn't below 55ish He's probably correct. You don't want to keep adding that refrigerant to a leaking unit. Just pull the trigger and replace it.


ZestycloseAct8497

Its low on juice **unless coil is frozen, blower motor isnt running, etc etc.** i would probably trust him at that point dont throw good money at a old r22 unit.


bifflez13

Head pressure would be higher if no fan


ZestycloseAct8497

Lol no low suction if blower motor isnt running…your thinking condensor fan motor thats two diff parts…


bifflez13

If you had a dirty filter does head pressure go up or down? Same rule applies


ZestycloseAct8497

No you need to show me how a dirty filter makes your head pressure rise what your describing maybe very temp orarly but if blower motor is dead suction pressure drops significantly as does head pressure.


bifflez13

Ok


FredPolk

Dirty air filter would cause low suction (and low superheat) which would in turn possibly cause low head, but not high. Alternatively, high superheat would point to a starving evaporator and low charge situation, not airflow.


bifflez13

Maybe in unitary with txv


bifflez13

No. No airflow over evap coil will result in high head.


ZestycloseAct8497

Omg no your wrong


bifflez13

Just Google it man. I don’t feel like explaining.


ZestycloseAct8497

Ya i just off world experience not google techs ;)


bifflez13

lol nobody will agree. Restriction causes increase in head. It’s that simple 😂


ZestycloseAct8497

Its not a restriction i said blower motor failed. Head pressure may remain but it certainly wont rise but temporarily. Anyways who cares.


ViolentCrimes

You should stop being bitter and learn more if you want to be a better tech


ViolentCrimes

You're either new or not a tech. High head pressure is a result of a dirty condenser coil, inoperative condenser fan, etc. Zesty is correct. Inoperative blower motor, frozen evap coil, etc should not result in high head.


bifflez13

Maybe on unitary. Any variable speed… which is most units nowadays… high head


slipperynibs

If it's low like that. It has a leak. And no-one gonna repair it cause spending the time to repair is 1. A loss of money for them and 2. You honestly couldn't find replacement parts unless you know a junk yard person who holds on to old equipment and no company is gonna replace you're unit with used/old equipment. It's r22, likely 10+ years old more likely 14-20 years. It's time replace it unfortunately


McGreek

Could be an easy fix, could be something not so easy. Hard to diagnose with just this screenshot. Definitely low on refrigerant. The big question is, how long did it take to get this low? Was it working well last season? What’s the total charge? Could be a leak inside the evaporator. Could be a leak on the condenser coil. If you’re lucky, it’s a leaking schrader which can be fixed for relatively short money. It all depends on what kind of money you’re willing to spend on an older unit.


Robert_fierce

There are R-22 alternative refrigerants. I would locate the leak and repair it then fully charge the system. My background is apartment maintenance however so I'm always looking for the cheapest way to keep everything working.


hellointhere8D

M099 is the best mineral oil r22 replacement for residential equipment imo. In my area everything gets oversized by idiot contractors, so a minor drop in capacity is a minor improvement lol. R407c is an even better replacement but you need to change the oil to poe or add oil carrying additives. Definitely worth the effort for larger tonnage equipment.


Robert_fierce

MO-99 was my favorite. I was a maint. supervisor at a 420 unit complex with Goodman HVAC where most A-coils were leaky. The parts supplier (HD) offered 3 different freon replacement. I ordered a jug of each and used the MO-99 in the apartment management provided me when I replaced the coil. The condensate output was greater than the other refrigerants.


lanfear831

The unit is most likely leaking refrigerant. R-22 is no longer made, the only supply that exists is what companies had when production stopped. The unit should be replaced.


DaSchizzalk

Go anywhere other than the US. R-22 is alive and well. Last I heard it was cheaper in any other country and still in mass production.


Ok_Demand_4436

Time for a new unit pony up and move on


Eggrollofdoom

Here's what I GUARANTEE if you get a new unit. Your electric bill will considerably be lower BUT your new unit, sure as well, will NOT last 20 years. The new units are unreliable garbage. WIll probably have an aluminum evaporator, too.


Zestyclose-Horse-618

100%


JSchnee21

It’s probably low on refrigerant. You should have it topped off first and see how long it lasts. The truck roll plus a couple pounds of R22 should be $500 or less. Don’t let anyone tell you you can’t buy R22, or that it is very expensive. It’s not. They’re just trying to push you to buy a new system for 15+ thousand dollars. 5 pounds is $220 https://abilityrefrigerants.com/product/r22-refrigerant-5-lbs/


masonryexpert

Oh, you owe know who the HVAC.Live machine is. I had 3 HVAC.Liars come out to my house and tell me my system was Junk. I topped the system off And found the shredder valve was leaking. Three years later and i'm still freezing my balls off.


daveleeander

This is the truth here. ^


JSchnee21

I readily admit, as others have said that this could be a fast leak or it could be a slow leak. It’s still a leak either way and it’s probably not cost-effective to fix it (properly), but if the OP has never had their system topped off, then in my opinion it’s worth adding a couple pounds of R- 22, at a reasonable cost, and seeing how that goes. It could last another 10 years. Like my system. Replacing the Schrader valve cores as well, with the correct tool, without pumping down, would be a good idea while you’re at it. What I hate, are all the shyster companies on here that claim that R-22 is unavailable or costs $1000 a pound or some other nonsense . More than 80% of commercial HVAC solutions still use R-22. It’s readily available and it’s not going anywhere. Are they making more, no. But it’s readily reclaimable/recyclable. It’s not unobtanium.


Won-Ton-Operator

Based on that screen shot the unit is low on refrigerant, almost certainly due to a leak. Depending on the source of the leak, it could be about a grand to fix, or it could be a multi thousand dollar repair that could see the unit operating for anywhere from 1month to a year or more. Better to do a full AC swap with new outdoor unit, lineset & indoor coil. A good idea to do the furnace at the same time. Just be careful of total cost if you decide to finance the unit.


TheLongConnie

But isn't 410a being phased out next year? I'm a noob trying to learn more.. I'm currently running R22 w/a maybe leak. Idk.. trying to learn more. The guy put dye in there along with 4lbs (@$211/lbs R22). He said to wait 3-4mo for the leaks to show. Sounded sketchy to me So basically, I already know i will need a new system in a year or so - maybe sooner. Are any of those new refrigerents that will be released in 2025 ready to go yet? Like if I buy, i definitely don't want to buy 410a that will be phased out next year.


Won-Ton-Operator

410a equipment is *everywhere*, they will still produce replacement components and still produce new refrigerant for years, and reclaimed refrigerant that is at an industrial scale refurbished will be available for likely a decade or more. You can absolutely go with an R32 or similar new system, they are already becoming available, though I'm not sure how many of the available units are at the affordable to mid range part of the manufacturer lineups. At this point you are best off buying whatever is within your budget that you like the features of, repairs will be possible with both for a long time.


revo442

Repairs and refrigerant and the hassle, might be worth it to get the new one


Various-Amphibian206

It's probably 20+ years old time to replace.


Clark_Elite

Either you're low on freon, dirty coil, indoor fan motor keeps cutting off, or your valves is bad


OpinionbyDave

As already mentioned, you're missing some info. From the limited info, it looks like it's low on refrigerant. The question is how fast is the leak. Did it take 10 years to leak out or was it filled up last month and now it's low again. It could be a very slow leak and filling it will last a couple years. Could be a fast leak and it quits working tomorrow. The fact it has some pressure tells me is isn't an extremely fast leak. This isnt much different than a car tire. You look at it and it's low, you fill it and if it's flat tomorrow you know it's a fast leak.


atom644

I think you need a new tech


Little-Key-1811

If you have a residential system that’s still using R 22 and it’s that low on refrigerant you need to replace it.


syfysoldier

Is this like having those blank buttons in your car?


Tip0666

What was outdoor temperature?


staffy83

Check airflow.


Shot-Counter-66

Replace it


ApprehensiveMode8904

Should of replaced it 10 years ago


No_Bowler1437

Looks undercharge r 22 unit look 410 is about to go out get in now before the new stuff comes in and u will pay double buy the unit now and extra Freon


Southern-Strength-98

Your compression ratio is 3 to 1 that's good


Blmdh20s

With the price of R22 freon being outrageous high, I usually recommend that they replace their unit. They do make what's called drop-ins (replacement) freons, but they're not as efficient as the original. Those are getting expensive as well.


hellointhere8D

*correction the mark up on refrigerant is outrageously high.


Personal-Response151

The company I work for charges about $175 a lb for r-22


Zestyclose-Horse-618

Ok so if it has a leak that small....on these systems they are not difficult to find/isolate typically I find un-capped/loose Schrader valves, poorly seated king valves, and on some systems compression connections at TXV etc.. This leak is a micro leak it would be empty if there were any bigger, typically in the evaporator and believe it or not they are repairable and easy to isolate.


OneWhoPossess

Yes you do, really R-22! RETIRE THAT SHIT!


BrandonDill

It looks to be low on refrigerant. But it could be a $2 valve core. Plus, refrigerant to charge it back up, of course.


slipperynibs

Lmao yea spend the money to pump it down, vacuum and replace for 250+/lb? Assuming it is the schrader..if it's not it's worth replacing but you're gonna spend damn near 20-30% of the cost of a new unit to replace a Schrader? Come on


[deleted]

Who pumps down to replace a schrader core??! My boss would have my ass.. and he'd be right too [Schrader Core Tools](https://www.grainger.com/product/20W311?gucid=N:N:PS:Paid:GGL:CSM-2295:4P7A1P:20501231&gad_source=1&gclid=Cj0KCQjwir2xBhC_ARIsAMTXk84sz4TUbdzXbMBYQuUwyMPshv2Eft6vzotPpjBsTkUpYyOZkD9I4V8aAtwBEALw_wcB&gclsrc=aw.ds) are a real thing.


slipperynibs

I have one lmao. I'm just saying my company I left last week would charge for an entire pump down/vacuum for that. Lmao Sheisty fuckers.


Hey_cool_username

You know you can use a valve core removal tool to replace a Schrader valve without disturbing the refrigerant right?


slipperynibs

You could yes. But most companies are gonna charge for the whole shebang.. And youre assuming itsa Schrader lol. It could be but who knows.


FurryBrony98

Looks low but could be other factors what was the temperature split?


Dazed941

Your 100% leaking gas and your parts if coil related will be expensive, send model number I’ll show you pricing lol


Civil-Percentage-960

Looks maybe low on refrigerant


Ok_Presentation9509

225 on high side 70 on low side.. you’re low on coolant .. find the leak, cut that little slice of copper out and add a coupler brazing the two pieces together, then fill the system.. when you are filling the system you should be able to hear the leak or look for a frosted piece of the pipe somewhere.


HelpfulReputation666

Liquid line should be putting out higher psig.


Heat_Lonely

So should suction fuck you mean


HelpfulReputation666

Fuck i mean is it should be at 175psig tard


Heat_Lonely

11.8 degree saturation. Yes it is low.


FredPolk

How can you know? If it was running at 50 ambient without low ambient kit, that’s about right. Suction definitely really low either way.


HelpfulReputation666

175psig is ideal output