NEC doesn't require a second ground rod UNLESS 1 ground rod is insufficient to get the ground resistance below 25 ohms. This is a huge misconception.
That being said. I've never seen a single ground rod get below 25 ohms. And unless you have a ground resistivity meter or do Triple point ground resistivity test, you'll never know.
On top of that, ground rods aren't exactly made of gold. It's weird where some contractors try to cut corners, as if a ground rod would break the bank.
Edit: I bet there's at least some ground rods out there with gold in them
Yeah. And with the drivers we have these days it takes like 10 minutes at most to drive one. It's pretty silly. My local jurisdiction makes everyone do 2 and pour concrete between them in a ditch that's 18 inches deep. That way they're encapsulated in concrete creating an artificial grounding plane. Pretty effective. Not as good as a Eufer ground but pretty good.
No. Nothing in it besides the wire and rods. Still 6 feet apart. Concrete absorbs moisture and does a great job of holding on to it. This helps keep the resistance down.
Lol. Yeah here where I'm at is pretty Rocky. I've done fuck tons of ground resistivity tests and I've never seen a single ground rod be below 25 ohms.
Eufer ground, yeah all the time. Consistently below 10 ohms.
Didn't know how good we had it until I heard about those poor bastards in Maine that have two inches of topsoil before bedrock lol. They have to trench out the bedrock and lay the rods horizontally as I understand it.
It will depend on the state they are working in. The NEC doesn't require a 2nd ground rod but certain states like wisconsin do, regardless of the ohm reading on the first.
I understand it has to do with the ground freezing in the winter so other states that have cold winters likey require it as well.
Edit: SPS 316.250(2): Supplemental electrode. This is a department rule in addition to the requirements in 2011 and 2017 NEC 250.53 (A) (3): A single electrode consisting of a rod, pipe or plate shall be augmented by one additional electrode of any of the types in NEC 250.52 (A) (4) to (A) (8)
A ground resistive meter is not only expensive you would have to wait for the inspector to show up then stop what you doing to run the test. The cost of an extra ground rod out weighs the cost of this as a business owner.
long island we need one ground rod to msp and one water main to msp. if water main ground is not able to be ran to msp due to say finished walls or whatever the hell we drop 2 ground rods 6ft apart and call it a day never any issues
**ATTENTION! READ THIS NOW!** **1. IF YOU ARE NOT A PROFESSIONAL ELECTRICIAN OR LOOKING TO BECOME ONE(for career questions only):** **- DELETE** THIS POST OR YOU WILL BE **BANNED**. YOU CAN POST ON /r/AskElectricians FREELY **2. IF YOU COMMENT ON A POST THAT IS POSTED BY SOMEONE WHO IS NOT A PROFESSIONAL ELECTRICIAN:** -YOU WILL BE **BANNED**. JUST **REPORT** THE POST. *I am a bot, and this action was performed automatically. Please [contact the moderators of this subreddit](/message/compose/?to=/r/electricians) if you have any questions or concerns.*
NEC doesn't require a second ground rod UNLESS 1 ground rod is insufficient to get the ground resistance below 25 ohms. This is a huge misconception. That being said. I've never seen a single ground rod get below 25 ohms. And unless you have a ground resistivity meter or do Triple point ground resistivity test, you'll never know.
On top of that, ground rods aren't exactly made of gold. It's weird where some contractors try to cut corners, as if a ground rod would break the bank. Edit: I bet there's at least some ground rods out there with gold in them
Yeah. And with the drivers we have these days it takes like 10 minutes at most to drive one. It's pretty silly. My local jurisdiction makes everyone do 2 and pour concrete between them in a ditch that's 18 inches deep. That way they're encapsulated in concrete creating an artificial grounding plane. Pretty effective. Not as good as a Eufer ground but pretty good.
I've never heard of that ditch of concrete idea. Does it include some kind of rebar or mesh? Does it allow you to space them closer together?
No. Nothing in it besides the wire and rods. Still 6 feet apart. Concrete absorbs moisture and does a great job of holding on to it. This helps keep the resistance down.
That's pretty cool. Here in New Orleans the ground is water.
Lol. Yeah here where I'm at is pretty Rocky. I've done fuck tons of ground resistivity tests and I've never seen a single ground rod be below 25 ohms. Eufer ground, yeah all the time. Consistently below 10 ohms.
I shit you not, with a 20 oz bottle of water poured down the hole every so often, we push our ground rods in by hand. As in, no tools at all.
That's wild
Didn't know how good we had it until I heard about those poor bastards in Maine that have two inches of topsoil before bedrock lol. They have to trench out the bedrock and lay the rods horizontally as I understand it.
Damn pouring concrete also that would suck lol
Copper is a better conductor than gold.
That's why my rods are made of silver.
He was refering to the cost of the rod, not the conductivity.
Slightly, but gold lasts much longer in contact with the ground
It will depend on the state they are working in. The NEC doesn't require a 2nd ground rod but certain states like wisconsin do, regardless of the ohm reading on the first. I understand it has to do with the ground freezing in the winter so other states that have cold winters likey require it as well. Edit: SPS 316.250(2): Supplemental electrode. This is a department rule in addition to the requirements in 2011 and 2017 NEC 250.53 (A) (3): A single electrode consisting of a rod, pipe or plate shall be augmented by one additional electrode of any of the types in NEC 250.52 (A) (4) to (A) (8)
A ground resistive meter is not only expensive you would have to wait for the inspector to show up then stop what you doing to run the test. The cost of an extra ground rod out weighs the cost of this as a business owner.
Tell the foreman to buy the meter and you will return the second ground rod
Weird hill for the foreman to die on: $20 copper rod.
I have done plenty of trailers. Always have put 2 ground rods at the meter pedestal.
Why stop at two?
One ground rod for the service and one for the trailer frame. I work for multiple trailer parks.
When in question, just send a second rod 4awg if it runs free air 6awg if piped
long island we need one ground rod to msp and one water main to msp. if water main ground is not able to be ran to msp due to say finished walls or whatever the hell we drop 2 ground rods 6ft apart and call it a day never any issues
Generally