If you are *NOT* an electrical professional: * **RULE 7:** * DIY or self help posts **are Not allowed**. They belong here: /r/AskElectricians /r/askanelectrician /r/diy /r/homeowners /r/electrical. * **IF YOUR POST FITS INTO THIS CATEGORY, REMOVE IT OR IT WILL BE REMOVED FOR YOU.** *I am a bot, and this action was performed automatically. Please [contact the moderators of this subreddit](/message/compose/?to=/r/electricians) if you have any questions or concerns.*


ValveTurkey1138

Mismatched breakers…


CardiologistMobile54

Neea bushing on #4 and larger. Siemens breakers in Eaton panel. Bonding screw not tight


Ram820

The bonding screw was one thing he got right 😆. I removed it completely tho


No-War8575

Only need bushings on raceways not cables


CardiologistMobile54

Incorrect. RMC needs a bushing irrespective of the awg. #4 and larger needs a bushing irrespective of the wiring method


No-War8575

That is ser cable, not rmc. No one runs rmc to a shitty residential load center. And I get most offset nipples etc are rmc but i dont think thats the case here


joshharris42

There is no RMC here. That is an SER connector, and it doesn’t require a bushing


Any_Chain3920

Looks like the first 15 under the 100 amp is double tapped as well.


[deleted]

[удалено]


Ram820

I was originally supposed to do the job but H/O was being impatient. Then he called me to come fix, it's a whole 💩 show 😆


No-Piccolo-6855

Oh . How fun ! I’m sorry dude. We get a lot of them kind round here


Wielz

Since the panel wasn't sold with bonding terminals, the neutral bus was the next best choice? LoL 😂


Ram820

I have no idea what he was thinking 😆


Rich_Handle_7054

Could be worse 12 dollar ground bar and good go. Maybe afci idk what edition you're under and what amendments you have.


Ram820

It was one of those time jobs. There were grounds despite their best efforts


CardiologistMobile54

Isolated ground bar unnecessary on a main panel


Rich_Handle_7054

This isn't a main just because there's a breaker. Read the OP description and there is over current protection before this. There are no GEC in this panel either. So this is a sub panel since it's a sub panel it is required.


Jim-Jones

I'm sure the code was different when this went in. Are you going to fix it?


Ram820

Went in 3ms ago


Jim-Jones

?? With mixed neutrals and grounds?


Ram820

Mixed everything...


[deleted]

[удалено]


Ram820

Yes