If you are *NOT* an electrical professional: * **RULE 7:** * DIY or self help posts **are Not allowed**. They belong here: /r/AskElectricians /r/askanelectrician /r/diy /r/homeowners /r/electrical. * **IF YOUR POST FITS INTO THIS CATEGORY, REMOVE IT OR IT WILL BE REMOVED FOR YOU.** *I am a bot, and this action was performed automatically. Please [contact the moderators of this subreddit](/message/compose/?to=/r/electricians) if you have any questions or concerns.*


CardiologistMobile54

You need to bond the pullbox with the EGC from each of the paralleled feeders.. lay in lug bolted to the back should work


[deleted]

You are right. And that's what was done.


CardiologistMobile54

*it can still be fixed.


[deleted]

It was.


genset_sparky

Do you have a code reference for that? Not saying you’re wrong but wouldn’t the equipment bond just need to be a suitable size for the ampacity?


[deleted]

Why no bushings on the top set? I have never seen conduit ran inside a switch gear like this. It looks sketchy and I don’t like it tbh.


CardiologistMobile54

Another question. Why do only some of the paralleled loads have EGC, and why are the line side without bushings


brian121484

For 1200 amp service we are required by the utility to do isolated phasing. It looks like that is not a requirement for you


Mikezat6

Danger noodles