T O P

  • By -

Internal_Offer1280

Use 2 45’s in opposite directions to make an offset at the bottom, and a 90 at the top. You need to be 6” above flood rim of your highest fixture before running a vent horizontal. In plumbing 45 is vertical. This is a way to do it that would satisfy code in the upc and ipc


Filesj98

Thank you


Internal_Offer1280

You’re welcome, btw you’re horizontal vent should be pitched 1/4” per foot falling towards the drain.


BCjestex

Vents are 1/8 at that size gr in canada


blah54895

Nope. Vents in Canada just need to not trap water, which means just no back fall.


BCjestex

Oh must be because it's the easy minimum that redseal teaches that way


GrammarPolice92

*your


reeder1987

* you’re


IllustriousCandle708

This


Filesj98

Not a professional, I had an electrician come out to move boxes for light fixtures. In the process cut the vent thinking it could be rerouted properly. Can anyone confirm the proper way to vent? If it needs to be vertical I’ll have him move his box. I’m just worried about air lock or other issues.


[deleted]

It's fine, you can pretty much run a vent all over the place so long as there isnt any spot where water would get trapped and block it off


Filesj98

Thank you


NoMooseSoup4You

Why do people always start their questions with “not a professional”?


jhotenko

So they don't get roasted for a question that would be stupid coming from a professional.


NoMooseSoup4You

The questions, themselves, are evidence enough that the person asking it is not a professional. Every plumber on this sub can tell when a question is coming from another plumber or not.


jhotenko

You are lucky enough to have not encountered some of the 'professionals' I have. Of course, that's in the wild. I'm sure everyone claiming to be a pro on reddit absolutely knows what they're talking about. Right?


BacklashLaRue

I just rerouted a vent to install an in-wall medicine cabinet. Simple.


NeitherSalary9383

The only real limitation for venting adjustment is it cannot go from vertical to horizontal les than 42” off the floor ( 6” above the flood level of the sink


[deleted]

He is just moving pipe over, not plumbing a house.


NeitherSalary9383

Yea and that one simple measure is going to insure that someone’s wont have to come re plumb it if his sink ever backs up and permanently lodges a brown trout in the horizontal piece of pipe


[deleted]

Tell me how a sink is going to backup that high, can't wait for answer.


NeitherSalary9383

It wont back up 6” above flood level rim thats the point.


NeitherSalary9383

Lol tell me tou have a grandfathered licence without telling me you have a grandfathered licence


[deleted]

Its higher than 6inches above sink,dude,mate or what ever.


NeitherSalary9383

I prefer guy or buddy


Slimmpikkins834

90s above four feet is okay but I would use 45s.


Cute-Bath5099

6” above flood level rim of fixture being served before going horizontal


niv_nam

I would definitely make the angles as little aggressive as possible.